#1
|
|||
|
|||
APC question
I have an 18 Ah APC for my computer.
My computer,LCD monitor, and modem are plugged into it. Battery indicator shows 29 mins of time left. Does that sound reasonable? I thought it would give much greater run time than with the original battery that it came with. Thanks, Andy |
Ads |
#2
|
|||
|
|||
APC question
In message , Andy
writes: I have an 18 Ah APC for my computer. My computer,LCD monitor, and modem are plugged into it. Battery indicator shows 29 mins of time left. Does that sound reasonable? Work it out! What does the "18 Ah" refer to: the capacity of a battery? What voltage battery? Assuming it's a 12V battery, 18 Ah @ 12V is 216 watt-hours; allowing for conversion inefficiency and the fact that the unit's own protection circuitry won't let the battery be run completely flat, less than 200 Watt-hours. What wattage do your computer, monitor, and modem consume? Assuming by modem you mean your ADSL modem/router, I'd guess 12-15W for that; monitor in the tens of watts - say 70-90; computer - well, since you mention a monitor, I assume it's a "desktop" not a laptop, so anything from say 150W to several times that. So 250 to 750 watts, being supplied by something with 200 Wh capacity. So 29 minutes sounds highly plausible. (I may be wildly out in my guesses for the consumption of the three items, but you get the idea.) I thought it would give much greater run time than with the original battery that it came with. What Ah was that? What run time did the system quote for that? And, is your "17 Ah" battery fully charged? Thanks, Andy -- J. P. Gilliver. UMRA: 1960/1985 MB++G()AL-IS-Ch++(p)Ar@T+H+Sh0!:`)DNAf I admire you British: when things get tough, you reach for humour. Not firearms. - Sigourney (Susan) Weaver, RT 2017/11/4-10 |
#3
|
|||
|
|||
APC question
Andy wrote:
I have an 18 Ah APC for my computer. My computer,LCD monitor, and modem are plugged into it. Battery indicator shows 29 mins of time left. Does that sound reasonable? I thought it would give much greater run time than with the original battery that it came with. Thanks, Andy Mine has 2 lead acid gel batteries, 270 watts, 400 VA. It is is good for for about 6 min. The servers at work each have massive battery packs. One server and small lcd is good for 10 min at most. |
#4
|
|||
|
|||
APC question
On Thursday, July 26, 2018 at 11:35:39 PM UTC-5, J. P. Gilliver (John) wrote:
In message , Andy writes: I have an 18 Ah APC for my computer. My computer,LCD monitor, and modem are plugged into it. Battery indicator shows 29 mins of time left. Does that sound reasonable? Work it out! What does the "18 Ah" refer to: the capacity of a battery? What voltage battery? Assuming it's a 12V battery, 18 Ah @ 12V is 216 watt-hours; allowing for conversion inefficiency and the fact that the unit's own protection circuitry won't let the battery be run completely flat, less than 200 Watt-hours. What wattage do your computer, monitor, and modem consume? Assuming by modem you mean your ADSL modem/router, I'd guess 12-15W for that; monitor in the tens of watts - say 70-90; computer - well, since you mention a monitor, I assume it's a "desktop" not a laptop, so anything from say 150W to several times that. So 250 to 750 watts, being supplied by something with 200 Wh capacity. So 29 minutes sounds highly plausible. (I may be wildly out in my guesses for the consumption of the three items, but you get the idea.) I thought it would give much greater run time than with the original battery that it came with. What Ah was that? What run time did the system quote for that? And, is your "17 Ah" battery fully charged? Thanks, Andy -- J. P. Gilliver. UMRA: 1960/1985 MB++G()AL-IS-Ch++(p)Ar@T+H+Sh0!:`)DNAf I admire you British: when things get tough, you reach for humour. Not firearms. - Sigourney (Susan) Weaver, RT 2017/11/4-10 Battery is 12 V. 18 Ah is the capacity. 22 inch monitor Of course the battery was fully charged. :-) Andy |
#5
|
|||
|
|||
APC question
Andy wrote:
I have an 18 Ah APC for my computer. My computer,LCD monitor, and modem are plugged into it. Battery indicator shows 29 mins of time left. Does that sound reasonable? I thought it would give much greater run time than with the original battery that it came with. Thanks, Andy Using my crystal ball on your equipment, the calc goes like this. The only real known in the equation, is that "1 hour has 60 minutes". 12V*18AH 60m ------------ * --- * eff = minutes of time 100W+30W+10W 1H 216WH 60m ----- * --- * eff = 93m * eff 140W 1H If eff was 0.7, time is 65m. I have no idea what the efficiency of the inverter on a UPS is. The 0.7 assumes a conventional switcher with no tricks. It really shouldn't be all that efficient, as it's switching 12V on the primary side, and that can't be all that good. We cannot assume the UPS is "too inefficient", as that would make the UPS heat up when the mains go off, and I've never noticed a bad heating effect on mine when the mains go off. The battery AH rating goes down at high current draw. Usually the product has a curve for derating purposes. The idle power of my best modern machine in the house, a desktop, is 60W. My newest machine is 100W to 110W at idle. I picked 100W for my example calc. The oldest machine in the house is 150W, and on that one, the power doesn't vary at all under high CPU load. The old machines are... just wasteful. Low MIPS, high watts. If gaming, whatever video card was in the old box, the power would double on the card. Your best bet is to find the curve for your product, to take some of the unknowns out of the calc. You can also use a Kill-A-Watt meter to determine AC load of each appliance connected to the UPS. https://www.homedepot.com/p/Kill-A-W...4400/202196386 Useful numbers from the Kill-A-Watt meter would be "Watts" and "PF". And the documentation for the UPS will have a different output limit for "Watts" versus "VA" loading (the ratio of those is PF), which is making a statement about the PF or Power Factor of the load(s). Old ATX PSUs have a PF of 0.65 to 0.7 or so (phase relationship of voltage to current on mains side). A modern ATX PSU with active PFC (PF correction) runs 0.99 and has the voltage and current are in-phase like on a light bulb load. Your three electrical loads all have switchers, so the PF should be similar for them. Again, a rough wild-guess pulled from thin air. If you have: 1) A clamp-on DC ammeter (clamped on battery lead). 2) A multimeter to measure battery voltage. 3) A Kill-A-Watt to measure output load power. you could get a value for eff yourself. Then the only remaining part of the puzzle is battery performance -- how the 18AH is degraded to 9AH if you draw 40A out of the battery during the event. A lighter electrical load, gets closer to the battery nominal AH rating during the discharge process. Also, it isn't really all that good of an idea to be running the battery pak flat for fun. That reduces the service life of the battery. By pampering mine, I got 10 years from it. Yes, the power goes off here, but I try to do an orderly shutdown in about 2 minutes if I can manage it. Only a small percentage of the 18AH gets used when you do it that way, and it doesn't take too much time to restore the charge. For car batteries, you only run them down 25% before you stop using it. So if a car battery was 18AH, you can only safely use 4.5AH (16 minutes worth) if the load switches itself off at a safe point in time. There are also deep discharge batteries for things like golf carts or forklifts, which have thicker plates, and more of their 18AH could be used without causing immediate battery failure. I don't know what that factor is for an SLA battery in a UPS. I treated my UPS like it was a car battery (calcium added to lead plates), just to be on the safe side. That will give you some idea how many variables there are. eff (switcher/inverter on output stage) battery derating curve at load point (not efficient at high load) percentage of battery used before UPS threshold trips out actual load and PF of item(s) making up the load Lots of variables. Paul |
#6
|
|||
|
|||
APC question
On Friday, July 27, 2018 at 2:44:20 AM UTC-5, Paul wrote:
Andy wrote: I have an 18 Ah APC for my computer. My computer,LCD monitor, and modem are plugged into it. Battery indicator shows 29 mins of time left. Does that sound reasonable? I thought it would give much greater run time than with the original battery that it came with. Thanks, Andy Using my crystal ball on your equipment, the calc goes like this. The only real known in the equation, is that "1 hour has 60 minutes". 12V*18AH 60m ------------ * --- * eff = minutes of time 100W+30W+10W 1H 216WH 60m ----- * --- * eff = 93m * eff 140W 1H If eff was 0.7, time is 65m. I have no idea what the efficiency of the inverter on a UPS is. The 0.7 assumes a conventional switcher with no tricks. It really shouldn't be all that efficient, as it's switching 12V on the primary side, and that can't be all that good. We cannot assume the UPS is "too inefficient", as that would make the UPS heat up when the mains go off, and I've never noticed a bad heating effect on mine when the mains go off. The battery AH rating goes down at high current draw. Usually the product has a curve for derating purposes. The idle power of my best modern machine in the house, a desktop, is 60W. My newest machine is 100W to 110W at idle. I picked 100W for my example calc. The oldest machine in the house is 150W, and on that one, the power doesn't vary at all under high CPU load. The old machines are... just wasteful. Low MIPS, high watts. If gaming, whatever video card was in the old box, the power would double on the card. Your best bet is to find the curve for your product, to take some of the unknowns out of the calc. You can also use a Kill-A-Watt meter to determine AC load of each appliance connected to the UPS. https://www.homedepot.com/p/Kill-A-W...4400/202196386 Useful numbers from the Kill-A-Watt meter would be "Watts" and "PF". And the documentation for the UPS will have a different output limit for "Watts" versus "VA" loading (the ratio of those is PF), which is making a statement about the PF or Power Factor of the load(s). Old ATX PSUs have a PF of 0.65 to 0.7 or so (phase relationship of voltage to current on mains side). A modern ATX PSU with active PFC (PF correction) runs 0.99 and has the voltage and current are in-phase like on a light bulb load. Your three electrical loads all have switchers, so the PF should be similar for them. Again, a rough wild-guess pulled from thin air. If you have: 1) A clamp-on DC ammeter (clamped on battery lead). 2) A multimeter to measure battery voltage. 3) A Kill-A-Watt to measure output load power. you could get a value for eff yourself. Then the only remaining part of the puzzle is battery performance -- how the 18AH is degraded to 9AH if you draw 40A out of the battery during the event. A lighter electrical load, gets closer to the battery nominal AH rating during the discharge process. Also, it isn't really all that good of an idea to be running the battery pak flat for fun. That reduces the service life of the battery. By pampering mine, I got 10 years from it. Yes, the power goes off here, but I try to do an orderly shutdown in about 2 minutes if I can manage it. Only a small percentage of the 18AH gets used when you do it that way, and it doesn't take too much time to restore the charge. For car batteries, you only run them down 25% before you stop using it. So if a car battery was 18AH, you can only safely use 4.5AH (16 minutes worth) if the load switches itself off at a safe point in time. There are also deep discharge batteries for things like golf carts or forklifts, which have thicker plates, and more of their 18AH could be used without causing immediate battery failure. I don't know what that factor is for an SLA battery in a UPS. I treated my UPS like it was a car battery (calcium added to lead plates), just to be on the safe side. That will give you some idea how many variables there are. eff (switcher/inverter on output stage) battery derating curve at load point (not efficient at high load) percentage of battery used before UPS threshold trips out actual load and PF of item(s) making up the load Lots of variables. Paul Thanks. I have a lot of info to go over. It ran for 1 hr. and showed 17 mins left. So I put it back on AC power to avoid data loss. I am happy with that time. :-) Andy |
#7
|
|||
|
|||
APC question
On Friday, July 27, 2018 at 2:44:20 AM UTC-5, Paul wrote:
Andy wrote: I have an 18 Ah APC for my computer. My computer,LCD monitor, and modem are plugged into it. Battery indicator shows 29 mins of time left. Does that sound reasonable? I thought it would give much greater run time than with the original battery that it came with. Thanks, Andy Using my crystal ball on your equipment, the calc goes like this. The only real known in the equation, is that "1 hour has 60 minutes". 12V*18AH 60m ------------ * --- * eff = minutes of time 100W+30W+10W 1H 216WH 60m ----- * --- * eff = 93m * eff 140W 1H If eff was 0.7, time is 65m. I have no idea what the efficiency of the inverter on a UPS is. The 0.7 assumes a conventional switcher with no tricks. It really shouldn't be all that efficient, as it's switching 12V on the primary side, and that can't be all that good. We cannot assume the UPS is "too inefficient", as that would make the UPS heat up when the mains go off, and I've never noticed a bad heating effect on mine when the mains go off. The battery AH rating goes down at high current draw. Usually the product has a curve for derating purposes. The idle power of my best modern machine in the house, a desktop, is 60W. My newest machine is 100W to 110W at idle. I picked 100W for my example calc. The oldest machine in the house is 150W, and on that one, the power doesn't vary at all under high CPU load. The old machines are... just wasteful. Low MIPS, high watts. If gaming, whatever video card was in the old box, the power would double on the card. Your best bet is to find the curve for your product, to take some of the unknowns out of the calc. You can also use a Kill-A-Watt meter to determine AC load of each appliance connected to the UPS. https://www.homedepot.com/p/Kill-A-W...4400/202196386 Useful numbers from the Kill-A-Watt meter would be "Watts" and "PF". And the documentation for the UPS will have a different output limit for "Watts" versus "VA" loading (the ratio of those is PF), which is making a statement about the PF or Power Factor of the load(s). Old ATX PSUs have a PF of 0.65 to 0.7 or so (phase relationship of voltage to current on mains side). A modern ATX PSU with active PFC (PF correction) runs 0.99 and has the voltage and current are in-phase like on a light bulb load. Your three electrical loads all have switchers, so the PF should be similar for them. Again, a rough wild-guess pulled from thin air. If you have: 1) A clamp-on DC ammeter (clamped on battery lead). 2) A multimeter to measure battery voltage. 3) A Kill-A-Watt to measure output load power. you could get a value for eff yourself. Then the only remaining part of the puzzle is battery performance -- how the 18AH is degraded to 9AH if you draw 40A out of the battery during the event. A lighter electrical load, gets closer to the battery nominal AH rating during the discharge process. Also, it isn't really all that good of an idea to be running the battery pak flat for fun. That reduces the service life of the battery. By pampering mine, I got 10 years from it. Yes, the power goes off here, but I try to do an orderly shutdown in about 2 minutes if I can manage it. Only a small percentage of the 18AH gets used when you do it that way, and it doesn't take too much time to restore the charge. For car batteries, you only run them down 25% before you stop using it. So if a car battery was 18AH, you can only safely use 4.5AH (16 minutes worth) if the load switches itself off at a safe point in time. There are also deep discharge batteries for things like golf carts or forklifts, which have thicker plates, and more of their 18AH could be used without causing immediate battery failure. I don't know what that factor is for an SLA battery in a UPS. I treated my UPS like it was a car battery (calcium added to lead plates), just to be on the safe side. That will give you some idea how many variables there are. eff (switcher/inverter on output stage) battery derating curve at load point (not efficient at high load) percentage of battery used before UPS threshold trips out actual load and PF of item(s) making up the load Lots of variables. Paul "Crystal ball" comments are unnecessary. I provide what info I think is necessary. If more is need, just ask away. Andy |
#8
|
|||
|
|||
APC question
Andy wrote:
On Friday, July 27, 2018 at 2:44:20 AM UTC-5, Paul wrote: Andy wrote: I have an 18 Ah APC for my computer. My computer,LCD monitor, and modem are plugged into it. Battery indicator shows 29 mins of time left. Does that sound reasonable? I thought it would give much greater run time than with the original battery that it came with. Thanks, Andy Using my crystal ball on your equipment, the calc goes like this. The only real known in the equation, is that "1 hour has 60 minutes". 12V*18AH 60m ------------ * --- * eff = minutes of time 100W+30W+10W 1H 216WH 60m ----- * --- * eff = 93m * eff 140W 1H If eff was 0.7, time is 65m. I have no idea what the efficiency of the inverter on a UPS is. The 0.7 assumes a conventional switcher with no tricks. It really shouldn't be all that efficient, as it's switching 12V on the primary side, and that can't be all that good. We cannot assume the UPS is "too inefficient", as that would make the UPS heat up when the mains go off, and I've never noticed a bad heating effect on mine when the mains go off. The battery AH rating goes down at high current draw. Usually the product has a curve for derating purposes. The idle power of my best modern machine in the house, a desktop, is 60W. My newest machine is 100W to 110W at idle. I picked 100W for my example calc. The oldest machine in the house is 150W, and on that one, the power doesn't vary at all under high CPU load. The old machines are... just wasteful. Low MIPS, high watts. If gaming, whatever video card was in the old box, the power would double on the card. Your best bet is to find the curve for your product, to take some of the unknowns out of the calc. You can also use a Kill-A-Watt meter to determine AC load of each appliance connected to the UPS. https://www.homedepot.com/p/Kill-A-W...4400/202196386 Useful numbers from the Kill-A-Watt meter would be "Watts" and "PF". And the documentation for the UPS will have a different output limit for "Watts" versus "VA" loading (the ratio of those is PF), which is making a statement about the PF or Power Factor of the load(s). Old ATX PSUs have a PF of 0.65 to 0.7 or so (phase relationship of voltage to current on mains side). A modern ATX PSU with active PFC (PF correction) runs 0.99 and has the voltage and current are in-phase like on a light bulb load. Your three electrical loads all have switchers, so the PF should be similar for them. Again, a rough wild-guess pulled from thin air. If you have: 1) A clamp-on DC ammeter (clamped on battery lead). 2) A multimeter to measure battery voltage. 3) A Kill-A-Watt to measure output load power. you could get a value for eff yourself. Then the only remaining part of the puzzle is battery performance -- how the 18AH is degraded to 9AH if you draw 40A out of the battery during the event. A lighter electrical load, gets closer to the battery nominal AH rating during the discharge process. Also, it isn't really all that good of an idea to be running the battery pak flat for fun. That reduces the service life of the battery. By pampering mine, I got 10 years from it. Yes, the power goes off here, but I try to do an orderly shutdown in about 2 minutes if I can manage it. Only a small percentage of the 18AH gets used when you do it that way, and it doesn't take too much time to restore the charge. For car batteries, you only run them down 25% before you stop using it. So if a car battery was 18AH, you can only safely use 4.5AH (16 minutes worth) if the load switches itself off at a safe point in time. There are also deep discharge batteries for things like golf carts or forklifts, which have thicker plates, and more of their 18AH could be used without causing immediate battery failure. I don't know what that factor is for an SLA battery in a UPS. I treated my UPS like it was a car battery (calcium added to lead plates), just to be on the safe side. That will give you some idea how many variables there are. eff (switcher/inverter on output stage) battery derating curve at load point (not efficient at high load) percentage of battery used before UPS threshold trips out actual load and PF of item(s) making up the load Lots of variables. Paul "Crystal ball" comments are unnecessary. I provide what info I think is necessary. If more is need, just ask away. Andy For some components of the math, the values need to be *measured*, as calculating leaves a wide error margin. I could easily be off by a factor of two, even if I knew what CPU your computer used. My new machine uses a 156W CPU, my older computer used a 36W CPU. Those are measured, full power numbers, not idle. Measured with the clamp-on ammeter. At idle, both processors use around 13W (12V at 1.1 amps). It's hard to say on some computers, where exactly the rest of the load is coming from. The Kill-A-Watt meter is cheap, and provides an accurate overall picture for individual AC powered devices. In fact, I would recommend a Kill-A-Watt as a "pre-purchase" before you go shopping for a UPS, to enable you to save money by buying just the right size of UPS for the job. The clamp-on ammeter answers questions such is "why is this motherboard getting hot" or "did Intel make a CPU that draws more than the rated power". Those kinds of questions. When the Kill-A-Watt gives a number you didn't expect, a $200 to $300 Clamp-On DC ammeter is able to give more details about individual subsystems within the computer. A $100 AC ammeter is not a substitute, because the "interesting" things inside the computer are DC. There are AC and AC/DC ammeters with jaws that clamp around wires, and for computer work, I need the DC. The DC also comes in handy for your car. I now know a defective starter motor on the car draws 150 amps, and causes the battery voltage to temporarily drop to 9V when the starter motor stalls. The clamp-on DC ammeter with "peak hold" told me the highest current flow number seen. You cannot easily do such a measurement with a shunt. And using shunts all over the place while working, is inconvenient. As far as the rest of the variables at play goes, some are pretty expensive to figure out on your own. Working out the battery efficiency curve experimentally, would probably destroy at least one battery doing all the charge/discharge cycles. The manufacturer derating curve (available per UPS model), is handy. By using stepwise refinement, you can make yourself a better number. ******* I don't really have a lot of tools here for electrical work. These are my main ones: 1) $100 multimeter (for volts and ohms, not current). You don't need all the ranges mine has, and you can get similar ones for $20. I can do Hfe on a transistor with mine. 2) $300 clamp-on AC/DC ammeter 10mA to 400A dynamic range Has been used for both AC and DC work. The 400A DC range allowed me to work on the car. 3) $30 Kill-A-Watt P4400. Cheap and accurate. Don't make a habit of running it near the upper limit, for more than a few minutes. You don't really need to check your electric kettle :-) If you want to experiment with dumb loads, test a 60W light bulb and see if it draws 60W. I generally draw the line at 500W loads. And that's about it. I don't own a scope. Or scope probes. A good scope costs $35000. Nice probes can cost $2000 (amplifier in probe tip). Cheap scopes aren't really worth owning. We had a $35000 scope on every lab bench at work. You can see my home budget is rather limited by comparison. Paul |
#9
|
|||
|
|||
APC question
In message , Paul
writes: [] And that's about it. I don't own a scope. Or scope probes. A good scope costs $35000. Nice probes can cost $2000 (amplifier in probe tip). Cheap scopes aren't really worth owning. We had a $35000 scope on every lab bench at work. You can see my home budget is rather limited by comparison. Paul Sometimes good, if a little old-fashioned in technology, ones come up when companies upgrade - especially if they have sell-to-staff arrangements. I have one that was good in its day (Tek 7000 series, with high-bandwidth [for then] plugins) through such a scheme; OK, it's bulky because it's CRT, but ... depends what you want to do with it. In an earlier generation, a colleague had one - Tek 545 series I _think_ - which was a _genuine_ two-beam tube (not simulated by rapid alternation): two timebases, so quite disconcerting to watch! -- J. P. Gilliver. UMRA: 1960/1985 MB++G()AL-IS-Ch++(p)Ar@T+H+Sh0!:`)DNAf 10.0 times 0.1 is hardly ever 1.0. |
#10
|
|||
|
|||
APC question
J. P. Gilliver (John) wrote:
In message , Paul writes: [] And that's about it. I don't own a scope. Or scope probes. A good scope costs $35000. Nice probes can cost $2000 (amplifier in probe tip). Cheap scopes aren't really worth owning. We had a $35000 scope on every lab bench at work. You can see my home budget is rather limited by comparison. Paul Sometimes good, if a little old-fashioned in technology, ones come up when companies upgrade - especially if they have sell-to-staff arrangements. I have one that was good in its day (Tek 7000 series, with high-bandwidth [for then] plugins) through such a scheme; OK, it's bulky because it's CRT, but ... depends what you want to do with it. In an earlier generation, a colleague had one - Tek 545 series I _think_ - which was a _genuine_ two-beam tube (not simulated by rapid alternation): two timebases, so quite disconcerting to watch! The 7000 series had some nice plug-in modules. My favorite (and not too common), was the diff amp that on the highest gain setting, could display your heartbeat while you held onto a pair of wires. It would do 1mV differential full scale or so. It probably wouldn't have been good enough for brain waves at 0.1mV. And I don't remember anyone trying that either (there never seem to be the right electrodes around when you need a pair). For computer work, or digital logic design, you need gear fast enough to display what's going on. Our kit stopped at 40GHz statistical sampling (20GHz Nyquist) back then, with rigid plumbing. And then you have to find someone to help you with sampling technique. We had one electronic component that had a solution for this. It was a chip with what I call "perfect IO", which is matched to the transmission line so there are no reflections (TTL logic, by comparison, isn't even remotely close to being "perfect IO" - ordinary logic signals are horrid). At the time, that chip interface didn't go too fast, maybe 2Gbit/sec or so as a bus lane of sorts. Well, one of our engineers phoned up the chip maker and said "what's the best way to verify the SI on this thing?". And the person on the other end of the line said "the chip has an internal sampling scope on that signal". The chip could take samples of its own signals, across the internal diff termination resistor. There was a little utility for pulling out the resulting waveform table, for display on a computer screen. I thought that was a great concept, but industry-wide, I don't think that caught on. And there was no paper trail for that feature either, so we didn't get to find out how it was implemented inside. The main chip spec made no mention of that, but their engineers were probably using that feature for verifying the perfection of their IO pad design in a chip lab. The engineer who got that answer, was kinda in a state of shock (that the answer would be so easy). It required zero prep work in the lab. ******* Back in those days, the fastest scope you could buy, was one of these. The Nyquist is 70GHz or so. The unit might use liquid nitrogen for cooling. Hypres scope https://ieeexplore.ieee.org/iel5/6/6373637/06448112.pdf In the promo picture there, the second scope from the left looks like "son of 7000", with the same sort of module layout. If it wasn't for the cryogenic requirement for that scope, I bet they would have sold a lot more. It's not that LN2 is particularly hard to come by, but finding a body to keep filling the dewar would be hard. It's like finding someone to water house plants at work. Paul |
#11
|
|||
|
|||
APC question
On Friday, July 27, 2018 at 3:13:37 PM UTC-5, Paul wrote:
Andy wrote: On Friday, July 27, 2018 at 2:44:20 AM UTC-5, Paul wrote: Andy wrote: I have an 18 Ah APC for my computer. My computer,LCD monitor, and modem are plugged into it. Battery indicator shows 29 mins of time left. Does that sound reasonable? I thought it would give much greater run time than with the original battery that it came with. Thanks, Andy Using my crystal ball on your equipment, the calc goes like this. The only real known in the equation, is that "1 hour has 60 minutes". 12V*18AH 60m ------------ * --- * eff = minutes of time 100W+30W+10W 1H 216WH 60m ----- * --- * eff = 93m * eff 140W 1H If eff was 0.7, time is 65m. I have no idea what the efficiency of the inverter on a UPS is. The 0.7 assumes a conventional switcher with no tricks. It really shouldn't be all that efficient, as it's switching 12V on the primary side, and that can't be all that good. We cannot assume the UPS is "too inefficient", as that would make the UPS heat up when the mains go off, and I've never noticed a bad heating effect on mine when the mains go off. The battery AH rating goes down at high current draw. Usually the product has a curve for derating purposes. The idle power of my best modern machine in the house, a desktop, is 60W. My newest machine is 100W to 110W at idle. I picked 100W for my example calc. The oldest machine in the house is 150W, and on that one, the power doesn't vary at all under high CPU load. The old machines are... just wasteful. Low MIPS, high watts. If gaming, whatever video card was in the old box, the power would double on the card. Your best bet is to find the curve for your product, to take some of the unknowns out of the calc. You can also use a Kill-A-Watt meter to determine AC load of each appliance connected to the UPS. https://www.homedepot.com/p/Kill-A-W...4400/202196386 Useful numbers from the Kill-A-Watt meter would be "Watts" and "PF". And the documentation for the UPS will have a different output limit for "Watts" versus "VA" loading (the ratio of those is PF), which is making a statement about the PF or Power Factor of the load(s). Old ATX PSUs have a PF of 0.65 to 0.7 or so (phase relationship of voltage to current on mains side). A modern ATX PSU with active PFC (PF correction) runs 0.99 and has the voltage and current are in-phase like on a light bulb load. Your three electrical loads all have switchers, so the PF should be similar for them. Again, a rough wild-guess pulled from thin air. If you have: 1) A clamp-on DC ammeter (clamped on battery lead). 2) A multimeter to measure battery voltage. 3) A Kill-A-Watt to measure output load power. you could get a value for eff yourself. Then the only remaining part of the puzzle is battery performance -- how the 18AH is degraded to 9AH if you draw 40A out of the battery during the event. A lighter electrical load, gets closer to the battery nominal AH rating during the discharge process. Also, it isn't really all that good of an idea to be running the battery pak flat for fun. That reduces the service life of the battery. By pampering mine, I got 10 years from it. Yes, the power goes off here, but I try to do an orderly shutdown in about 2 minutes if I can manage it. Only a small percentage of the 18AH gets used when you do it that way, and it doesn't take too much time to restore the charge. For car batteries, you only run them down 25% before you stop using it. So if a car battery was 18AH, you can only safely use 4.5AH (16 minutes worth) if the load switches itself off at a safe point in time. There are also deep discharge batteries for things like golf carts or forklifts, which have thicker plates, and more of their 18AH could be used without causing immediate battery failure. I don't know what that factor is for an SLA battery in a UPS. I treated my UPS like it was a car battery (calcium added to lead plates), just to be on the safe side. That will give you some idea how many variables there are. eff (switcher/inverter on output stage) battery derating curve at load point (not efficient at high load) percentage of battery used before UPS threshold trips out actual load and PF of item(s) making up the load Lots of variables. Paul "Crystal ball" comments are unnecessary. I provide what info I think is necessary. If more is need, just ask away. Andy For some components of the math, the values need to be *measured*, as calculating leaves a wide error margin. I could easily be off by a factor of two, even if I knew what CPU your computer used. My new machine uses a 156W CPU, my older computer used a 36W CPU. Those are measured, full power numbers, not idle. Measured with the clamp-on ammeter. At idle, both processors use around 13W (12V at 1.1 amps). It's hard to say on some computers, where exactly the rest of the load is coming from. The Kill-A-Watt meter is cheap, and provides an accurate overall picture for individual AC powered devices. In fact, I would recommend a Kill-A-Watt as a "pre-purchase" before you go shopping for a UPS, to enable you to save money by buying just the right size of UPS for the job. The clamp-on ammeter answers questions such is "why is this motherboard getting hot" or "did Intel make a CPU that draws more than the rated power". Those kinds of questions. When the Kill-A-Watt gives a number you didn't expect, a $200 to $300 Clamp-On DC ammeter is able to give more details about individual subsystems within the computer. A $100 AC ammeter is not a substitute, because the "interesting" things inside the computer are DC. There are AC and AC/DC ammeters with jaws that clamp around wires, and for computer work, I need the DC. The DC also comes in handy for your car. I now know a defective starter motor on the car draws 150 amps, and causes the battery voltage to temporarily drop to 9V when the starter motor stalls. The clamp-on DC ammeter with "peak hold" told me the highest current flow number seen. You cannot easily do such a measurement with a shunt. And using shunts all over the place while working, is inconvenient. As far as the rest of the variables at play goes, some are pretty expensive to figure out on your own. Working out the battery efficiency curve experimentally, would probably destroy at least one battery doing all the charge/discharge cycles. The manufacturer derating curve (available per UPS model), is handy. By using stepwise refinement, you can make yourself a better number. ******* I don't really have a lot of tools here for electrical work. These are my main ones: 1) $100 multimeter (for volts and ohms, not current). You don't need all the ranges mine has, and you can get similar ones for $20. I can do Hfe on a transistor with mine. 2) $300 clamp-on AC/DC ammeter 10mA to 400A dynamic range Has been used for both AC and DC work. The 400A DC range allowed me to work on the car. 3) $30 Kill-A-Watt P4400. Cheap and accurate. Don't make a habit of running it near the upper limit, for more than a few minutes. You don't really need to check your electric kettle :-) If you want to experiment with dumb loads, test a 60W light bulb and see if it draws 60W. I generally draw the line at 500W loads. And that's about it. I don't own a scope. Or scope probes. A good scope costs $35000. Nice probes can cost $2000 (amplifier in probe tip). Cheap scopes aren't really worth owning. We had a $35000 scope on every lab bench at work. You can see my home budget is rather limited by comparison. Paul I have order a kill o watt. It seems to be a worthwhile tool to have. I also have a RMS multimeter. Andy |
#12
|
|||
|
|||
APC question
On Saturday, July 28, 2018 at 2:56:47 PM UTC-5, Andy wrote:
On Friday, July 27, 2018 at 3:13:37 PM UTC-5, Paul wrote: Andy wrote: On Friday, July 27, 2018 at 2:44:20 AM UTC-5, Paul wrote: Andy wrote: I have an 18 Ah APC for my computer. My computer,LCD monitor, and modem are plugged into it. Battery indicator shows 29 mins of time left. Does that sound reasonable? I thought it would give much greater run time than with the original battery that it came with. Thanks, Andy Using my crystal ball on your equipment, the calc goes like this. The only real known in the equation, is that "1 hour has 60 minutes". 12V*18AH 60m ------------ * --- * eff = minutes of time 100W+30W+10W 1H 216WH 60m ----- * --- * eff = 93m * eff 140W 1H If eff was 0.7, time is 65m. I have no idea what the efficiency of the inverter on a UPS is. The 0.7 assumes a conventional switcher with no tricks. It really shouldn't be all that efficient, as it's switching 12V on the primary side, and that can't be all that good. We cannot assume the UPS is "too inefficient", as that would make the UPS heat up when the mains go off, and I've never noticed a bad heating effect on mine when the mains go off. The battery AH rating goes down at high current draw. Usually the product has a curve for derating purposes. The idle power of my best modern machine in the house, a desktop, is 60W. My newest machine is 100W to 110W at idle. I picked 100W for my example calc. The oldest machine in the house is 150W, and on that one, the power doesn't vary at all under high CPU load. The old machines are... just wasteful. Low MIPS, high watts. If gaming, whatever video card was in the old box, the power would double on the card. Your best bet is to find the curve for your product, to take some of the unknowns out of the calc. You can also use a Kill-A-Watt meter to determine AC load of each appliance connected to the UPS. https://www.homedepot.com/p/Kill-A-W...4400/202196386 Useful numbers from the Kill-A-Watt meter would be "Watts" and "PF". And the documentation for the UPS will have a different output limit for "Watts" versus "VA" loading (the ratio of those is PF), which is making a statement about the PF or Power Factor of the load(s). Old ATX PSUs have a PF of 0.65 to 0.7 or so (phase relationship of voltage to current on mains side). A modern ATX PSU with active PFC (PF correction) runs 0.99 and has the voltage and current are in-phase like on a light bulb load. Your three electrical loads all have switchers, so the PF should be similar for them. Again, a rough wild-guess pulled from thin air. If you have: 1) A clamp-on DC ammeter (clamped on battery lead). 2) A multimeter to measure battery voltage. 3) A Kill-A-Watt to measure output load power. you could get a value for eff yourself. Then the only remaining part of the puzzle is battery performance -- how the 18AH is degraded to 9AH if you draw 40A out of the battery during the event. A lighter electrical load, gets closer to the battery nominal AH rating during the discharge process. Also, it isn't really all that good of an idea to be running the battery pak flat for fun. That reduces the service life of the battery. By pampering mine, I got 10 years from it. Yes, the power goes off here, but I try to do an orderly shutdown in about 2 minutes if I can manage it. Only a small percentage of the 18AH gets used when you do it that way, and it doesn't take too much time to restore the charge. For car batteries, you only run them down 25% before you stop using it. So if a car battery was 18AH, you can only safely use 4.5AH (16 minutes worth) if the load switches itself off at a safe point in time. There are also deep discharge batteries for things like golf carts or forklifts, which have thicker plates, and more of their 18AH could be used without causing immediate battery failure. I don't know what that factor is for an SLA battery in a UPS. I treated my UPS like it was a car battery (calcium added to lead plates), just to be on the safe side. That will give you some idea how many variables there are. eff (switcher/inverter on output stage) battery derating curve at load point (not efficient at high load) percentage of battery used before UPS threshold trips out actual load and PF of item(s) making up the load Lots of variables. Paul "Crystal ball" comments are unnecessary. I provide what info I think is necessary. If more is need, just ask away. Andy For some components of the math, the values need to be *measured*, as calculating leaves a wide error margin. I could easily be off by a factor of two, even if I knew what CPU your computer used. My new machine uses a 156W CPU, my older computer used a 36W CPU. Those are measured, full power numbers, not idle. Measured with the clamp-on ammeter. At idle, both processors use around 13W (12V at 1.1 amps). It's hard to say on some computers, where exactly the rest of the load is coming from. The Kill-A-Watt meter is cheap, and provides an accurate overall picture for individual AC powered devices. In fact, I would recommend a Kill-A-Watt as a "pre-purchase" before you go shopping for a UPS, to enable you to save money by buying just the right size of UPS for the job. The clamp-on ammeter answers questions such is "why is this motherboard getting hot" or "did Intel make a CPU that draws more than the rated power". Those kinds of questions. When the Kill-A-Watt gives a number you didn't expect, a $200 to $300 Clamp-On DC ammeter is able to give more details about individual subsystems within the computer. A $100 AC ammeter is not a substitute, because the "interesting" things inside the computer are DC. There are AC and AC/DC ammeters with jaws that clamp around wires, and for computer work, I need the DC. The DC also comes in handy for your car. I now know a defective starter motor on the car draws 150 amps, and causes the battery voltage to temporarily drop to 9V when the starter motor stalls. The clamp-on DC ammeter with "peak hold" told me the highest current flow number seen. You cannot easily do such a measurement with a shunt. And using shunts all over the place while working, is inconvenient. As far as the rest of the variables at play goes, some are pretty expensive to figure out on your own. Working out the battery efficiency curve experimentally, would probably destroy at least one battery doing all the charge/discharge cycles. The manufacturer derating curve (available per UPS model), is handy. By using stepwise refinement, you can make yourself a better number. ******* I don't really have a lot of tools here for electrical work. These are my main ones: 1) $100 multimeter (for volts and ohms, not current). You don't need all the ranges mine has, and you can get similar ones for $20. I can do Hfe on a transistor with mine. 2) $300 clamp-on AC/DC ammeter 10mA to 400A dynamic range Has been used for both AC and DC work. The 400A DC range allowed me to work on the car. 3) $30 Kill-A-Watt P4400. Cheap and accurate. Don't make a habit of running it near the upper limit, for more than a few minutes. You don't really need to check your electric kettle :-) If you want to experiment with dumb loads, test a 60W light bulb and see if it draws 60W. I generally draw the line at 500W loads. And that's about it. I don't own a scope. Or scope probes. A good scope costs $35000. Nice probes can cost $2000 (amplifier in probe tip). Cheap scopes aren't really worth owning. We had a $35000 scope on every lab bench at work. You can see my home budget is rather limited by comparison. Paul I have order a kill o watt. It seems to be a worthwhile tool to have. I also have a RMS multimeter. Andy Kill o watt shows 90 watts for computer during startup about 60 watts after desktop shows monitor uses 75 watts. |
#13
|
|||
|
|||
APC question
Andy wrote:
On Saturday, July 28, 2018 at 2:56:47 PM UTC-5, Andy wrote: On Friday, July 27, 2018 at 3:13:37 PM UTC-5, Paul wrote: Andy wrote: On Friday, July 27, 2018 at 2:44:20 AM UTC-5, Paul wrote: Andy wrote: I have an 18 Ah APC for my computer. My computer,LCD monitor, and modem are plugged into it. Battery indicator shows 29 mins of time left. Does that sound reasonable? I thought it would give much greater run time than with the original battery that it came with. Thanks, Andy Using my crystal ball on your equipment, the calc goes like this. The only real known in the equation, is that "1 hour has 60 minutes". 12V*18AH 60m ------------ * --- * eff = minutes of time 100W+30W+10W 1H 216WH 60m ----- * --- * eff = 93m * eff 140W 1H If eff was 0.7, time is 65m. I have no idea what the efficiency of the inverter on a UPS is. The 0.7 assumes a conventional switcher with no tricks. It really shouldn't be all that efficient, as it's switching 12V on the primary side, and that can't be all that good. We cannot assume the UPS is "too inefficient", as that would make the UPS heat up when the mains go off, and I've never noticed a bad heating effect on mine when the mains go off. The battery AH rating goes down at high current draw. Usually the product has a curve for derating purposes. The idle power of my best modern machine in the house, a desktop, is 60W. My newest machine is 100W to 110W at idle. I picked 100W for my example calc. The oldest machine in the house is 150W, and on that one, the power doesn't vary at all under high CPU load. The old machines are... just wasteful. Low MIPS, high watts. If gaming, whatever video card was in the old box, the power would double on the card. Your best bet is to find the curve for your product, to take some of the unknowns out of the calc. You can also use a Kill-A-Watt meter to determine AC load of each appliance connected to the UPS. https://www.homedepot.com/p/Kill-A-W...4400/202196386 Useful numbers from the Kill-A-Watt meter would be "Watts" and "PF". And the documentation for the UPS will have a different output limit for "Watts" versus "VA" loading (the ratio of those is PF), which is making a statement about the PF or Power Factor of the load(s). Old ATX PSUs have a PF of 0.65 to 0.7 or so (phase relationship of voltage to current on mains side). A modern ATX PSU with active PFC (PF correction) runs 0.99 and has the voltage and current are in-phase like on a light bulb load. Your three electrical loads all have switchers, so the PF should be similar for them. Again, a rough wild-guess pulled from thin air. If you have: 1) A clamp-on DC ammeter (clamped on battery lead). 2) A multimeter to measure battery voltage. 3) A Kill-A-Watt to measure output load power. you could get a value for eff yourself. Then the only remaining part of the puzzle is battery performance -- how the 18AH is degraded to 9AH if you draw 40A out of the battery during the event. A lighter electrical load, gets closer to the battery nominal AH rating during the discharge process. Also, it isn't really all that good of an idea to be running the battery pak flat for fun. That reduces the service life of the battery. By pampering mine, I got 10 years from it. Yes, the power goes off here, but I try to do an orderly shutdown in about 2 minutes if I can manage it. Only a small percentage of the 18AH gets used when you do it that way, and it doesn't take too much time to restore the charge. For car batteries, you only run them down 25% before you stop using it. So if a car battery was 18AH, you can only safely use 4.5AH (16 minutes worth) if the load switches itself off at a safe point in time. There are also deep discharge batteries for things like golf carts or forklifts, which have thicker plates, and more of their 18AH could be used without causing immediate battery failure. I don't know what that factor is for an SLA battery in a UPS. I treated my UPS like it was a car battery (calcium added to lead plates), just to be on the safe side. That will give you some idea how many variables there are. eff (switcher/inverter on output stage) battery derating curve at load point (not efficient at high load) percentage of battery used before UPS threshold trips out actual load and PF of item(s) making up the load Lots of variables. Paul "Crystal ball" comments are unnecessary. I provide what info I think is necessary. If more is need, just ask away. Andy For some components of the math, the values need to be *measured*, as calculating leaves a wide error margin. I could easily be off by a factor of two, even if I knew what CPU your computer used. My new machine uses a 156W CPU, my older computer used a 36W CPU. Those are measured, full power numbers, not idle. Measured with the clamp-on ammeter. At idle, both processors use around 13W (12V at 1.1 amps). It's hard to say on some computers, where exactly the rest of the load is coming from. The Kill-A-Watt meter is cheap, and provides an accurate overall picture for individual AC powered devices. In fact, I would recommend a Kill-A-Watt as a "pre-purchase" before you go shopping for a UPS, to enable you to save money by buying just the right size of UPS for the job. The clamp-on ammeter answers questions such is "why is this motherboard getting hot" or "did Intel make a CPU that draws more than the rated power". Those kinds of questions. When the Kill-A-Watt gives a number you didn't expect, a $200 to $300 Clamp-On DC ammeter is able to give more details about individual subsystems within the computer. A $100 AC ammeter is not a substitute, because the "interesting" things inside the computer are DC. There are AC and AC/DC ammeters with jaws that clamp around wires, and for computer work, I need the DC. The DC also comes in handy for your car. I now know a defective starter motor on the car draws 150 amps, and causes the battery voltage to temporarily drop to 9V when the starter motor stalls. The clamp-on DC ammeter with "peak hold" told me the highest current flow number seen. You cannot easily do such a measurement with a shunt. And using shunts all over the place while working, is inconvenient. As far as the rest of the variables at play goes, some are pretty expensive to figure out on your own. Working out the battery efficiency curve experimentally, would probably destroy at least one battery doing all the charge/discharge cycles. The manufacturer derating curve (available per UPS model), is handy. By using stepwise refinement, you can make yourself a better number. ******* I don't really have a lot of tools here for electrical work. These are my main ones: 1) $100 multimeter (for volts and ohms, not current). You don't need all the ranges mine has, and you can get similar ones for $20. I can do Hfe on a transistor with mine. 2) $300 clamp-on AC/DC ammeter 10mA to 400A dynamic range Has been used for both AC and DC work. The 400A DC range allowed me to work on the car. 3) $30 Kill-A-Watt P4400. Cheap and accurate. Don't make a habit of running it near the upper limit, for more than a few minutes. You don't really need to check your electric kettle :-) If you want to experiment with dumb loads, test a 60W light bulb and see if it draws 60W. I generally draw the line at 500W loads. And that's about it. I don't own a scope. Or scope probes. A good scope costs $35000. Nice probes can cost $2000 (amplifier in probe tip). Cheap scopes aren't really worth owning. We had a $35000 scope on every lab bench at work. You can see my home budget is rather limited by comparison. Paul I have order a kill o watt. It seems to be a worthwhile tool to have. I also have a RMS multimeter. Andy Kill o watt shows 90 watts for computer during startup about 60 watts after desktop shows monitor uses 75 watts. Which means your runtime estimate calculation should have a lesser number now. When picking a UPS, both the watt and VA numbers can be used. As UPSes usually have a max watt number and a max VA number on output. The holdup times should be in a graph for the product, on the product web page. The graph may be in the user manual, but not always. Paul |
#14
|
|||
|
|||
APC question
On Monday, July 30, 2018 at 4:13:36 PM UTC-5, Paul wrote:
Andy wrote: On Saturday, July 28, 2018 at 2:56:47 PM UTC-5, Andy wrote: On Friday, July 27, 2018 at 3:13:37 PM UTC-5, Paul wrote: Andy wrote: On Friday, July 27, 2018 at 2:44:20 AM UTC-5, Paul wrote: Andy wrote: I have an 18 Ah APC for my computer. My computer,LCD monitor, and modem are plugged into it. Battery indicator shows 29 mins of time left. Does that sound reasonable? I thought it would give much greater run time than with the original battery that it came with. Thanks, Andy Using my crystal ball on your equipment, the calc goes like this. The only real known in the equation, is that "1 hour has 60 minutes". 12V*18AH 60m ------------ * --- * eff = minutes of time 100W+30W+10W 1H 216WH 60m ----- * --- * eff = 93m * eff 140W 1H If eff was 0.7, time is 65m. I have no idea what the efficiency of the inverter on a UPS is. The 0.7 assumes a conventional switcher with no tricks. It really shouldn't be all that efficient, as it's switching 12V on the primary side, and that can't be all that good. We cannot assume the UPS is "too inefficient", as that would make the UPS heat up when the mains go off, and I've never noticed a bad heating effect on mine when the mains go off. The battery AH rating goes down at high current draw. Usually the product has a curve for derating purposes. The idle power of my best modern machine in the house, a desktop, is 60W. My newest machine is 100W to 110W at idle. I picked 100W for my example calc. The oldest machine in the house is 150W, and on that one, the power doesn't vary at all under high CPU load. The old machines are... just wasteful. Low MIPS, high watts. If gaming, whatever video card was in the old box, the power would double on the card. Your best bet is to find the curve for your product, to take some of the unknowns out of the calc. You can also use a Kill-A-Watt meter to determine AC load of each appliance connected to the UPS. https://www.homedepot.com/p/Kill-A-W...4400/202196386 Useful numbers from the Kill-A-Watt meter would be "Watts" and "PF". And the documentation for the UPS will have a different output limit for "Watts" versus "VA" loading (the ratio of those is PF), which is making a statement about the PF or Power Factor of the load(s). Old ATX PSUs have a PF of 0.65 to 0.7 or so (phase relationship of voltage to current on mains side). A modern ATX PSU with active PFC (PF correction) runs 0.99 and has the voltage and current are in-phase like on a light bulb load. Your three electrical loads all have switchers, so the PF should be similar for them. Again, a rough wild-guess pulled from thin air. If you have: 1) A clamp-on DC ammeter (clamped on battery lead). 2) A multimeter to measure battery voltage. 3) A Kill-A-Watt to measure output load power. you could get a value for eff yourself. Then the only remaining part of the puzzle is battery performance -- how the 18AH is degraded to 9AH if you draw 40A out of the battery during the event. A lighter electrical load, gets closer to the battery nominal AH rating during the discharge process. Also, it isn't really all that good of an idea to be running the battery pak flat for fun. That reduces the service life of the battery. By pampering mine, I got 10 years from it. Yes, the power goes off here, but I try to do an orderly shutdown in about 2 minutes if I can manage it. Only a small percentage of the 18AH gets used when you do it that way, and it doesn't take too much time to restore the charge. For car batteries, you only run them down 25% before you stop using it. So if a car battery was 18AH, you can only safely use 4.5AH (16 minutes worth) if the load switches itself off at a safe point in time. There are also deep discharge batteries for things like golf carts or forklifts, which have thicker plates, and more of their 18AH could be used without causing immediate battery failure. I don't know what that factor is for an SLA battery in a UPS. I treated my UPS like it was a car battery (calcium added to lead plates), just to be on the safe side. That will give you some idea how many variables there are. eff (switcher/inverter on output stage) battery derating curve at load point (not efficient at high load) percentage of battery used before UPS threshold trips out actual load and PF of item(s) making up the load Lots of variables. Paul "Crystal ball" comments are unnecessary. I provide what info I think is necessary. If more is need, just ask away. Andy For some components of the math, the values need to be *measured*, as calculating leaves a wide error margin. I could easily be off by a factor of two, even if I knew what CPU your computer used. My new machine uses a 156W CPU, my older computer used a 36W CPU. Those are measured, full power numbers, not idle. Measured with the clamp-on ammeter. At idle, both processors use around 13W (12V at 1.1 amps). It's hard to say on some computers, where exactly the rest of the load is coming from. The Kill-A-Watt meter is cheap, and provides an accurate overall picture for individual AC powered devices. In fact, I would recommend a Kill-A-Watt as a "pre-purchase" before you go shopping for a UPS, to enable you to save money by buying just the right size of UPS for the job. The clamp-on ammeter answers questions such is "why is this motherboard getting hot" or "did Intel make a CPU that draws more than the rated power". Those kinds of questions. When the Kill-A-Watt gives a number you didn't expect, a $200 to $300 Clamp-On DC ammeter is able to give more details about individual subsystems within the computer. A $100 AC ammeter is not a substitute, because the "interesting" things inside the computer are DC. There are AC and AC/DC ammeters with jaws that clamp around wires, and for computer work, I need the DC. The DC also comes in handy for your car. I now know a defective starter motor on the car draws 150 amps, and causes the battery voltage to temporarily drop to 9V when the starter motor stalls. The clamp-on DC ammeter with "peak hold" told me the highest current flow number seen. You cannot easily do such a measurement with a shunt. And using shunts all over the place while working, is inconvenient. As far as the rest of the variables at play goes, some are pretty expensive to figure out on your own. Working out the battery efficiency curve experimentally, would probably destroy at least one battery doing all the charge/discharge cycles. The manufacturer derating curve (available per UPS model), is handy. By using stepwise refinement, you can make yourself a better number. ******* I don't really have a lot of tools here for electrical work. These are my main ones: 1) $100 multimeter (for volts and ohms, not current). You don't need all the ranges mine has, and you can get similar ones for $20. I can do Hfe on a transistor with mine. 2) $300 clamp-on AC/DC ammeter 10mA to 400A dynamic range Has been used for both AC and DC work. The 400A DC range allowed me to work on the car. 3) $30 Kill-A-Watt P4400. Cheap and accurate. Don't make a habit of running it near the upper limit, for more than a few minutes. You don't really need to check your electric kettle :-) If you want to experiment with dumb loads, test a 60W light bulb and see if it draws 60W. I generally draw the line at 500W loads. And that's about it. I don't own a scope. Or scope probes. A good scope costs $35000. Nice probes can cost $2000 (amplifier in probe tip). Cheap scopes aren't really worth owning. We had a $35000 scope on every lab bench at work. You can see my home budget is rather limited by comparison. Paul I have order a kill o watt. It seems to be a worthwhile tool to have. I also have a RMS multimeter. Andy Kill o watt shows 90 watts for computer during startup about 60 watts after desktop shows monitor uses 75 watts. Which means your runtime estimate calculation should have a lesser number now. When picking a UPS, both the watt and VA numbers can be used. As UPSes usually have a max watt number and a max VA number on output. The holdup times should be in a graph for the product, on the product web page. The graph may be in the user manual, but not always. Paul O.K. I ran it for an hour on the APS and shut it down when it showed I had around 15 minutes left. But the remaining time value kept changing. I think it is only somewhat accurate. My settings when On UPS power, When computer is inactive for 10 minutes, it is put to sleep. When UPS power critically low, computer is shutdown. When inactive for 10 mins, display is put to sleep. Andy |
#15
|
|||
|
|||
APC question
In message , Andy
writes: [144 lines snipped!!!] O.K. I ran it for an hour on the APS and shut it down when it showed I had around 15 minutes left. Where does this "show" - on a display on the UPS/APS, or on the computer (via a serial or USB link to the UPS/APS)? But the remaining time value kept changing. I think it is only somewhat accurate. Or, like time to finish a multi-file move or copy, it might change as the load changes. Might be worth having Task Manager open and seeing if there's any (inverse) correlation between CPU load and projected time left. My settings when On UPS power, When computer is inactive for 10 minutes, it is put to sleep. When UPS power critically low, computer is shutdown. When inactive for 10 mins, display is put to sleep. Andy -- J. P. Gilliver. UMRA: 1960/1985 MB++G()AL-IS-Ch++(p)Ar@T+H+Sh0!:`)DNAf Does my Bradshaw look big in this? |
|